Testing, Adjusting & Balancing (TAB)
TAB sets every air terminal and water branch to its design flow, so each space gets the cooling it was designed for and fans and pumps don't waste energy. It only works on a system that is clean, complete and stable.
Before you balance
- Ductwork leakage-tested, filters in, dampers open; pipework flushed and cleaned, strainers clean, air vented.
- Fans and pumps running at their design settings; controls held in a fixed mode.
- Calibrated instruments: flow hood, pitot tube and manometer, anemometer, differential pressure meter for valves.
- Design data ready: terminal and valve schedules with design flows.
Air balancing
- Measure the total fan flow with a duct traverse, then each branch and terminal.
- Use the proportional method: set terminals on a branch to the same % of design, then adjust branch dampers, then the fan.
- Leave the index run (the one with the highest resistance) fully open; trim the others.
- Typical acceptance is about ±10 % at terminals; check your specification.
Water balancing
- Measure flow at balancing valves from ΔP and Kv, or with PICVs check the minimum ΔP across each valve.
- Balance proportionally from the index circuit back to the pump, then set the pump speed or impeller.
- Check chilled-water ΔT at coils and chillers. Low ΔT (return water too cold) means too much flow, dirty coils or wrong valves, and it wastes chiller and pump capacity.
- Typical acceptance is about −5 % to +10 % of design flow; check your specification.
Common TAB problems
| Symptom | Likely cause |
|---|---|
| Terminal can't reach design | Closed or missing damper, duct leakage, dirty filter, fan speed too low |
| All terminals high | Fan too fast; reduce speed after balancing |
| Branch can't reach design flow | Air in pipe, blocked strainer, closed valve, pump head too low |
| Low CHW ΔT | Over-flow, bypass open, 3-way valves, dirty coils |
| Readings unstable | Controls hunting, measuring too close to a fitting |