Chilled Water ΔT and Flow

Chilled water flow is set by the cooling load and the temperature difference between supply and return.

Key relationship

  • Flow (L/s) = Load (kW) ÷ (4.19 × ΔT), with water's specific heat 4.19 kJ/kg·K.
  • Classic design: 6.7 °C supply, 12.2 °C return (ΔT ≈ 5.5 K). Many district cooling schemes use larger ΔT such as 8–10 K.
  • Doubling ΔT halves the flow, so pipes and pumps get smaller and pumping energy drops.

Low ΔT syndrome

  • Return water comes back colder than designed, so chillers run at part load while pumps work hard.
  • Common causes: oversized or uncontrolled coils, three-way valves, dirty coils, bypass lines.
Good to knowDistrict cooling providers in Qatar penalise low return temperatures. Coil and valve selection affects your client's bill.