Fire Pumps & Water Supplies
A sprinkler or hydrant system is only as good as its water supply. In most Gulf buildings that means a dedicated fire water tank and a fire pump set that must start and run, every time, for the whole duration of a fire.
Water supply
- Fire water storage sized for the largest demand (sprinklers plus hose) for the required duration, often in a dedicated tank or a reserved volume of a shared tank.
- Civil defence rules set minimum volumes and connections (for example fire brigade inlets); check them early because tank size affects the structure.
- Keep the fire reserve protected so domestic use can never draw it down.
Pumps and controllers
- NFPA 20: a listed fire pump whose curve stays within 140 % of rated pressure at churn and gives at least 65 % at 150 % flow.
- Typical sets: an electric main pump, a diesel standby pump and a jockey pump that keeps the system pressurised so the main pump doesn't start for small leaks.
- Listed fire pump controllers; electric supply arranged so that it stays live in a fire (supply taken ahead of the main switch or from a reliable source, per the code).
- Diesel pumps need fuel for the required run time, ventilation, cooling and batteries.
Testing
- Acceptance test with the maker and the authority: flow at churn, 100 % and 150 %, start on pressure drop, transfer of power, alarms.
- Weekly or monthly churn runs and an annual flow test under NFPA 25 (or the local equivalent).
- Record pressures and flows each time; a falling curve is an early warning.