Controls & automation

Field Instruments, 4–20 mA & HART

Field instruments turn pressure, temperature, flow and level into signals the control system can use. The 4–20 mA loop has survived decades of digital alternatives because it is simple, robust and tells you when a wire breaks.

The 4–20 mA loop

  • 4 mA = bottom of the range (LRV), 20 mA = top (URV). The live zero means 0 mA is a fault, not a reading.
  • Most transmitters are 2-wire: the same pair carries power and signal, so the supply must cover the receiver, cable and any barrier (see the loop budget calculator).
  • NAMUR NE 43 fixes the levels: 3.8–20.5 mA is measurement, 3.6 mA or less and 21 mA or more signal a fault. Configure the control system to match.
  • Shielded twisted pairs, shields earthed at one end (usually the control panel), and analogue cables kept apart from power cables.

HART and digital buses

  • HART adds a digital signal on top of the 4–20 mA: diagnostics, configuration and extra variables without new wiring. It needs about 250 Ω (at least 230 Ω) in the loop.
  • Fieldbuses (FOUNDATION Fieldbus, PROFIBUS PA) and industrial Ethernet replace many analogue loops on large plants.
  • Whatever the signal, the instrument index and loop diagrams must match the field.

Selection and calibration

  • Choose by measuring principle, range, accuracy, process connection, materials, and hazardous-area certificate where needed.
  • Temperature: RTDs (Pt100, IEC 60751) for accuracy; thermocouples for high temperatures.
  • Calibrate against traceable references and record as-found and as-left values; keep the certificates for handover.
  • Install with the hook-up drawings: impulse line slopes, manifolds, isolation valves and access for maintenance.

4–20 mA reference points (linear)

SignalPercent of range
4 mA0 %
8 mA25 %
12 mA50 %
16 mA75 %
20 mA100 %
≤ 3.6 or ≥ 21 mAFault (NE 43)
Good to knowWhen a reading looks wrong, measure the loop current first. It tells you in seconds whether the problem is in the field or in the system.

Use with this guide

Found an error? Tell us

Describe the problem briefly (the wrong value, the right one, and the reference if you have it). The page name is sent automatically.