Cable Derating Factors

Tabulated cable ratings assume reference conditions. Real installations are hotter, more crowded or buried, so the rating is multiplied by correction factors.

The usual factors

  • Ambient temperature (Ca): reference is 30 °C in air and 20 °C in ground. Gulf summers need factors for 45–50 °C.
  • Grouping (Cg): cables bunched or laid together heat each other.
  • Soil thermal resistivity: dry desert sand insulates far more than the 2.5 K·m/W reference.
  • Depth of laying for buried cables.
  • Thermal insulation where cables pass through insulated walls or roofs.

Applying them

  • Multiply all applicable factors: Iz = It × Ca × Cg × …
  • Size the cable so Iz ≥ In ≥ Ib (design current ≤ device rating ≤ derated capacity).
  • Then check voltage drop and short-circuit withstand, which may force a larger size.
Good to knowUse the project specification's ambient temperature. Many Qatar projects specify 50 °C for outdoor and 40 °C for indoor non-conditioned spaces.