Tonnage, COP and EER

Cooling capacity and efficiency appear in different units on every datasheet. These are the conversions that matter.

Conversions

  • 1 TR (ton of refrigeration) = 12,000 BTU/h = 3.517 kW of cooling.
  • COP = cooling output (kW) ÷ electrical input (kW). Dimensionless.
  • EER = cooling (BTU/h) ÷ electrical input (W). EER = COP × 3.412.
  • kW/TR = electrical input per ton, common for chillers. kW/TR = 3.517 ÷ COP.

Electrical impact

  • A chiller with 0.65 kW/TR on a 500 TR plant draws about 325 kW at full load.
  • Use the chiller's starting method and inrush data when sizing generators and transformers.
Good to knowAsk whether the efficiency figure is at full load or IPLV/ESEER (part-load). Part-load numbers look better and suit annual energy estimates, not electrical sizing.