Tonnage, COP and EER
Cooling capacity and efficiency appear in different units on every datasheet. These are the conversions that matter.
Conversions
- 1 TR (ton of refrigeration) = 12,000 BTU/h = 3.517 kW of cooling.
- COP = cooling output (kW) ÷ electrical input (kW). Dimensionless.
- EER = cooling (BTU/h) ÷ electrical input (W). EER = COP × 3.412.
- kW/TR = electrical input per ton, common for chillers. kW/TR = 3.517 ÷ COP.
Electrical impact
- A chiller with 0.65 kW/TR on a 500 TR plant draws about 325 kW at full load.
- Use the chiller's starting method and inrush data when sizing generators and transformers.