Testing and Commissioning of Utility Networks
Each utility owner accepts a network only after its own tests, witnessed and recorded. Plan the tests by section, so the road works are not held up.
Typical tests
- Gravity sewer and storm: air or water test between manholes, CCTV survey, deflection check for flexible pipes, manhole leak test.
- Water and TSE mains: hydrostatic pressure test, flushing, disinfection and bacteriological samples (water).
- Power cables: insulation resistance, sheath test, high-voltage test for MV, phasing and continuity.
- Telecom and ITS ducts: mandrel (proving) test, draw rope check; fibre loss and OTDR after cabling.
- Compaction: field density tests on each backfill layer.
Plan the testing
- A test tracker by section and chainage, with the planned date, the witness and the result.
- Test before the road layers close the trench; re-opening a finished road costs far more than waiting a day.
- Calibrated instruments with certificates on site for every test.
- Agree the test method and acceptance values in writing before the first test.
Use with this guide
Network Test Tracker by Section
Pressure, air, CCTV, mandrel and compaction tests per section with dates, witness, result and progress per network
- How to use
- Tests
- Tests (SAMPLE)