Fire protection

Sprinkler Systems

Automatic sprinklers are the most effective fire protection most buildings have: each head opens on its own when heated and controls the fire where it starts. Their design depends on what the building holds and how it is used.

System types

  • Wet pipe: pipes full of water; the most common and the most reliable.
  • Dry pipe: pipes filled with air where water could freeze (rare in the Gulf except cold stores).
  • Pre-action: needs a detection signal before water enters the pipes; used for data centres and archives.
  • Deluge: open heads that all discharge together; used for high-hazard areas such as transformers and fuel stores.

Design basis

  • NFPA 13 groups occupancies into light, ordinary (groups 1 and 2) and extra hazard (groups 1 and 2); storage has its own rules.
  • The density/area method sets the water per m² over a design area at the most remote part of the system, plus a hose allowance and a duration.
  • The hydraulic calculation proves the pipes and the supply deliver that demand with pressure to spare.
  • Local civil defence codes (e.g. Saudi SBC 801, the UAE Fire and Life Safety Code, Qatar Civil Defence requirements) adopt NFPA with local changes; follow the approved version.

Heads and installation

  • Heads have a K-factor (flow = K √P), a temperature rating and a response type (standard or quick response).
  • Keep spacing, distances to walls and clearances below heads within the listing; obstructions such as ducts and trays are a common failure.
  • Pipe supports, seismic bracing where required, flushing and a hydrostatic test (NFPA 13: 200 psi or 50 psi above working pressure for 2 hours) before commissioning.
Good to knowWalk the ceiling void before the ceiling closes. A duct installed after the sprinkler layout can block a head for the life of the building.

Use with this guide