Protection Selectivity

Selectivity (also called discrimination) means that when a fault occurs, only the protective device immediately upstream of it opens. The rest of the installation stays energised.

Methods

  • Current selectivity: upstream device has a higher instantaneous setting than the fault current at the downstream device.
  • Time selectivity: upstream device has an intentional short-time delay (needs adequate short-time withstand, Icw).
  • Energy selectivity: current-limiting downstream devices let through too little energy to trip the upstream one.
  • Zone selective interlocking (ZSI): breakers communicate so the one nearest the fault trips without delay.

In practice

  • Use the manufacturer's selectivity tables. They state total or partial selectivity up to a given fault current.
  • Partial selectivity is only valid up to the stated limit current; above it both devices may trip.
  • Plot time-current curves in ETAP or the maker's software for MV and main LV levels.
Good to knowOn data centres and hospitals, the client usually requires total selectivity. Confirm this in the design basis before buying switchgear.