LV Installation Testing (IEC 60364-6 / BS 7671)
Before a new LV installation is energised and handed over, it is inspected and tested to prove it is safe. The order matters: dead tests first, with the supply isolated, then live tests once it is safe to connect.
Inspection and dead tests
- Visual inspection first: correct devices, labels, IP ratings, cable support, segregation, terminations and barriers.
- Continuity of protective conductors (R1 + R2, or R2) on every circuit, and of main and supplementary bonding.
- Insulation resistance between live conductors and to earth, at the test voltage for the circuit (e.g. 500 V DC for 230/400 V); disconnect sensitive equipment first.
- Polarity: switches and protective devices in the line conductor, correct connections at sockets and lamp holders.
- Earth electrode resistance where the installation has its own electrode (TT systems).
Live tests
- Earth fault loop impedance (Zs) at the furthest point of each circuit, compared with the maximum for the protective device.
- Prospective fault current at the origin and boards, compared with the breaking capacity of the devices.
- RCD tests: trip time at the rated residual current (and the test button).
- Phase sequence on three-phase supplies, and functional tests of switchgear, interlocks and controls.
Records
- A schedule of test results for every board and circuit, signed by the tester and witness.
- Instrument serial numbers and calibration dates on every sheet.
- Defects recorded, fixed and retested before energisation.
- As-built drawings, circuit charts in each board, and the certificate or completion report the authority requires.
Minimum insulation resistance (IEC 60364-6 Table 6A)
| Circuit | Test voltage | Minimum |
|---|---|---|
| SELV / PELV | 250 V DC | 0.5 MΩ |
| Up to 500 V (incl. 230/400 V) | 500 V DC | 1 MΩ |
| Above 500 V | 1000 V DC | 1 MΩ |