LV Installation Testing (IEC 60364-6 / BS 7671)

Before a new LV installation is energised and handed over, it is inspected and tested to prove it is safe. The order matters: dead tests first, with the supply isolated, then live tests once it is safe to connect.

Inspection and dead tests

  • Visual inspection first: correct devices, labels, IP ratings, cable support, segregation, terminations and barriers.
  • Continuity of protective conductors (R1 + R2, or R2) on every circuit, and of main and supplementary bonding.
  • Insulation resistance between live conductors and to earth, at the test voltage for the circuit (e.g. 500 V DC for 230/400 V); disconnect sensitive equipment first.
  • Polarity: switches and protective devices in the line conductor, correct connections at sockets and lamp holders.
  • Earth electrode resistance where the installation has its own electrode (TT systems).

Live tests

  • Earth fault loop impedance (Zs) at the furthest point of each circuit, compared with the maximum for the protective device.
  • Prospective fault current at the origin and boards, compared with the breaking capacity of the devices.
  • RCD tests: trip time at the rated residual current (and the test button).
  • Phase sequence on three-phase supplies, and functional tests of switchgear, interlocks and controls.

Records

  • A schedule of test results for every board and circuit, signed by the tester and witness.
  • Instrument serial numbers and calibration dates on every sheet.
  • Defects recorded, fixed and retested before energisation.
  • As-built drawings, circuit charts in each board, and the certificate or completion report the authority requires.

Minimum insulation resistance (IEC 60364-6 Table 6A)

CircuitTest voltageMinimum
SELV / PELV250 V DC0.5 MΩ
Up to 500 V (incl. 230/400 V)500 V DC1 MΩ
Above 500 V1000 V DC1 MΩ
Good to knowTest Zs before you hand the circuit over, not after the ceiling is closed. A loose neutral or earth found at testing costs minutes; found after handover it costs a ceiling.