Controls & automation

FAT, SAT & Loop Checks

Controls are tested in stages, each proving something the earlier stage couldn't. Skipping one moves the problem to a later stage, where it is slower and more expensive to find.

FAT: factory acceptance test

  • At the supplier's works, before shipping: hardware, software, graphics, logic and redundancy, using simulated signals.
  • Follow an approved FAT procedure (IEC 62381 gives a framework) with the client present; record punch items and close them before shipping.

Loop checks

  • After installation and cable testing: check each loop from the field device to the screen.
  • Inject or simulate the signal (e.g. 4, 12, 20 mA) and confirm the tag, range, units, alarms and fault level in the system.
  • Stroke valves and check open / close feedback; check motor start, stop and running signals.
  • Sign each loop on its loop diagram; un-checked loops are the first thing to chase before start-up.

SAT and functional tests

  • Site acceptance test: the installed system working as a whole, with field devices, networks and interfaces.
  • Test sequences, interlocks and the cause and effect matrix line by line; witness safety functions with the client.
  • Hand over as-built loop diagrams, the I/O list, final software backups and passwords.
Good to knowBack up the controller software at every stage and label the backups with date and version. The one time you need it, it will be the most important file on the project.

Use with this guide

Found an error? Tell us

Describe the problem briefly (the wrong value, the right one, and the reference if you have it). The page name is sent automatically.