FAT, SAT & Loop Checks
Controls are tested in stages, each proving something the earlier stage couldn't. Skipping one moves the problem to a later stage, where it is slower and more expensive to find.
FAT: factory acceptance test
- At the supplier's works, before shipping: hardware, software, graphics, logic and redundancy, using simulated signals.
- Follow an approved FAT procedure (IEC 62381 gives a framework) with the client present; record punch items and close them before shipping.
Loop checks
- After installation and cable testing: check each loop from the field device to the screen.
- Inject or simulate the signal (e.g. 4, 12, 20 mA) and confirm the tag, range, units, alarms and fault level in the system.
- Stroke valves and check open / close feedback; check motor start, stop and running signals.
- Sign each loop on its loop diagram; un-checked loops are the first thing to chase before start-up.
SAT and functional tests
- Site acceptance test: the installed system working as a whole, with field devices, networks and interfaces.
- Test sequences, interlocks and the cause and effect matrix line by line; witness safety functions with the client.
- Hand over as-built loop diagrams, the I/O list, final software backups and passwords.