A façade is tested several times before handover: as a mock-up in a laboratory, as installed on site, and through its anchors and sealants. Each stage catches what the previous one couldn't.
Performance mock-up (PMU)
- A full-size sample of the typical façade tested in an independent laboratory before production.
- Usual sequence: air infiltration (ASTM E283), static water (ASTM E331), dynamic water (AAMA 501.1), structural (ASTM E330), sometimes seismic or thermal cycling; CWCT test sequences are an alternative.
- Failures are fixed and retested; the approved mock-up becomes the benchmark for production.
Site tests
- Field water hose test (AAMA 501.2) on installed joints, typically on a set percentage of the façade, starting early so problems are found before most panels are installed.
- Field air and water tests on a chamber (ASTM E783 / E1105) where specified.
- Pull-out tests on anchors, and adhesion tests on structural and weather sealants (e.g. ASTM C1521).
- Visual inspection of brackets, fixings, gaskets, sealant joints and fire stopping before they are covered.
Records
- Keep test reports, inspection records and photos by elevation and floor.
- Track leaks and repairs on a façade issues log until closed and retested.
- Hand over maintenance instructions for sealants, gaskets and glass replacement.