Roads & pavements

Earthworks, Subgrade & Compaction

Compaction pushes soil particles together so the layer is stronger, stiffer and less permeable. Every layer is compared with a laboratory test of the same material.

Laboratory tests

  • Proctor test gives the maximum dry density (MDD) and optimum moisture content (OMC). The modified test uses more energy than the standard test, and is usual for roads.
  • CBR (California Bearing Ratio) measures strength for pavement design and material acceptance, often after soaking.
  • Grading, plasticity (Atterberg limits) and, in the Gulf, salt and gypsum content to accept or reject the fill source.

Placing and compacting

  • Place in layers of the specified thickness; common practice is about 150–250 mm compacted, but the spec and the roller decide.
  • Bring the material near OMC before rolling. Too dry will not compact; too wet will pump and rut.
  • Roll with the approved number of passes from a trial, then test before the next layer.
  • Proof-roll the subgrade with a loaded truck to find soft spots; remove and replace them.

Field testing and Gulf issues

  • Sand cone and nuclear gauge tests give field density and moisture. Calibrate the gauge for the local material.
  • Compare dry density with MDD to get the relative compaction and check moisture against OMC.
  • Sabkha, collapsible and gypsum-rich soils need special treatment: removal, geotextile separation or stabilisation.
  • Water for compaction may be restricted if saline; follow the specification.
Good to knowMake sure the MDD you compare with is from the same material source. A new borrow pit means a new Proctor test.

Use with this guide

Found an error? Tell us

Describe the problem briefly (the wrong value, the right one, and the reference if you have it). The page name is sent automatically.