Controls & automation

Building Management Systems (BMS)

In Gulf buildings the BMS runs the cooling plant, air handling, ventilation and lighting, and watches dozens of other systems. Most problems at handover come from integration: two systems that were each tested but never talked to each other.

What a BMS does

  • Controls HVAC plant and terminal units: chillers or district cooling ETS, pumps, AHUs, FCUs, fans, with schedules and set points.
  • Monitors other systems through integration: generators, UPS, lifts, fire alarm status, meters, leak detection.
  • Logs trends, raises alarms and produces energy reports from electricity, chilled-water and water meters.

Points list and protocols

  • The points list is the BMS's I/O list: every hardwired and integrated point with type, range, alarm limits and trend settings.
  • BACnet (ASHRAE 135 / ISO 16484-5) is the usual building protocol; Modbus (RTU or TCP) is common for meters, drives and packages.
  • Ask every package supplier for the protocol, the register or object map and who configures it, before the order is placed.

Fire and life-safety interfaces

  • Fire alarm to BMS is usually monitoring only; smoke control, fan shutdown and damper commands are hardwired from the fire alarm system per the cause and effect matrix.
  • Life-safety functions must not rely on the BMS network; the authority (civil defence) witnesses these tests.
  • Commission the interfaces with both contractors present, using the cause and effect matrix as the test script.
Good to knowWrite the integration matrix (which system talks to which, by what protocol, who configures each side) in the first month. It is the cheapest document on the project and saves the most arguments.