Mechanical & HVAC

HVAC Commissioning: Stages & Documents

Commissioning proves that HVAC systems are installed correctly and perform as designed, under real operating conditions, before the client takes them over. It runs in stages, and each stage has to be signed before the next starts.

The stages

  • Pre-commissioning (static): installation checks, flushing and chemical cleaning, pressure and duct leakage tests, electrical tests, point-to-point BMS checks. Nothing runs yet.
  • Start-up: first run of fans, pumps and chillers with the manufacturer's representative, checking rotation, currents, vibration and safeties.
  • Testing, adjusting and balancing (TAB): air and water flows set to design at every terminal and valve.
  • Functional performance tests (FPT): control sequences, alarms and modes tested against the sequence of operations.
  • Integrated systems tests (IST): HVAC tested together with fire alarm, smoke control, power failure and generators.
  • Seasonal or deferred tests where design conditions can't be reached at handover.

Key documents

  • Commissioning plan and programme, with responsibilities and witness points.
  • Method statements and pre-functional checklists for each equipment type.
  • Flushing, pressure test, duct leakage and TAB reports with instrument calibration certificates.
  • FPT and IST scripts with signed results, and a commissioning issues log.
  • O&M manuals, as-built drawings, training records and the final commissioning report.

Who does what

  • The contractor and specialists carry out the work and fill in the records.
  • A commissioning manager or commissioning authority plans, coordinates and checks; the consultant and client witness.
  • Manufacturers' representatives start up major plant (chillers, AHUs with integrated controls, VFDs).
  • The facilities team should attend tests and training: they will run the building.

Typical references

TopicCommon references
ProcessASHRAE Guideline 0 / Standard 202, CIBSE Code M
Air systemsCIBSE Code A, BSRIA BG 49, ASHRAE 111
Water systemsCIBSE Code W, BSRIA BG 2, BG 29 (flushing and cleaning)
ControlsCIBSE Code C
Duct leakageSMACNA, EN 12237 / DW/143
Good to knowStart the commissioning plan at design stage. Valves, test points and access panels that were never drawn can't be balanced or tested later.

Use with this guide

Found an error? Tell us

Describe the problem briefly (the wrong value, the right one, and the reference if you have it). The page name is sent automatically.