Testing & Commissioning Water and Sewer Pipes
Every pipe is tested before it is backfilled fully and put into service. Water mains must also be disinfected and pass bacteriological tests before they supply anyone.
Water mains
- Hydrostatic pressure test to the specified test pressure and duration (methods in EN 805, AWWA C600 or the authority's rules), with allowable loss or make-up water calculated per the method.
- Test in sections, with thrust blocks cured and air removed.
- Disinfection with chlorine at the specified dose and contact time, then flushing to normal residual.
- Bacteriological samples must pass before connection to the live network.
Gravity sewers
- Air or water test on each pipe section between manholes (methods in EN 1610 or the local standard).
- Manholes tested for watertightness.
- CCTV survey to find cracks, joint gaps, deflection, roots and sags before handover.
- Deflection check for flexible pipes (mandrel test) where specified.
Records
- Test certificates signed by the contractor and consultant, with gauge calibration.
- As-built drawings with invert levels, valve and manhole positions.
- Lab reports for bacteriological samples, with chain of custody.
- CCTV reports and videos with defect coding.