ELV

Public Address & Voice Alarm

A public address (PA) system plays paging and background music. A voice alarm (VA) system is a life safety system that broadcasts evacuation messages on a fire alarm signal. Most buildings combine both in one PA/VA system.

How it works

  • Speakers are connected in parallel on a 100 V line (70 V in some markets). Each speaker has a transformer with power taps, e.g. 1.5, 3 or 6 W.
  • The building is divided into zones so messages can be sent to one area or all areas.
  • Priority order: fire alarm evacuation, then emergency microphone, then general paging, then background music.

Voice alarm requirements

  • Control equipment to EN 54-16 and loudspeakers to EN 54-24; design to BS 5839-8 or NFPA 72 chapter 24.
  • Use A/B wiring (two circuits per area interleaved) so one cable fault does not silence a whole area.
  • Fire-resistant cable, a standby amplifier and battery standby are required.
  • Pre-recorded messages in the languages of the building users, usually Arabic and English in the region.

Sound quality

  • Speech intelligibility is measured as STI. A common target for voice alarm is an STI of at least 0.50.
  • The sound level must be clearly above background noise; in very reverberant areas add more speakers at lower power rather than fewer loud ones.
  • Acoustic modelling software (e.g. EASE) helps in atria, halls and car parks.

Typical speaker tap settings

AreaTypical tap
Offices, corridors1.5 – 3 W ceiling speaker
Car parks, plant rooms6 – 10 W horn or projector
Atria and hallsColumn or line array
Outdoor areasWeatherproof horn, 10 – 30 W
Good to knowMeasure the line impedance of each zone before connecting the amplifier. It finds short circuits and wrong taps before they damage equipment.