MV Switchgear, Transformer & Cable Testing
An MV substation is energised only after every piece of equipment has passed its site tests and the protection has been proven to trip. The tests confirm that nothing was damaged in transport or installation and that everything was connected as designed.
Switchgear and protection
- Insulation resistance and the specified power-frequency withstand test on the main circuit.
- Contact (micro-ohm) resistance of breakers and busbar joints; breaker timing where specified.
- Mechanical operation and interlocks (earth switch, doors, racking).
- CT and VT ratio, polarity and magnetisation tests; wiring checks to relays and meters.
- Secondary injection of every relay to the approved settings, then primary injection or trip tests to prove the whole chain, including trip circuits and batteries.
Transformers
- Insulation resistance of windings (HV–LV, HV–E, LV–E), often with a polarisation index.
- Turns ratio on every tap and vector group check.
- Winding resistance on every tap.
- For oil-filled units: oil breakdown voltage (BDV), levels, leaks, Buchholz and temperature devices. For dry types: winding temperature sensors and fans.
MV cables
- Insulation resistance before and after the high-voltage test.
- Sheath test to check the outer sheath wasn't damaged during laying (IEC 60229).
- After-installation withstand test: AC or VLF (very low frequency), at the voltage and duration in IEC 60502-2 / IEEE 400.2 or the specification.
- Phasing and identification at both ends before connection.
Safety for HV testing
| Rule | Why |
|---|---|
| Permit to work and lock-out | No one can energise or approach the equipment |
| Barriers and warning signs at both ends | Cables have two ends: the far end is live during tests |
| Discharge and earth after every DC or VLF test | Cables and windings store a dangerous charge |
| Calibrated instruments, competent testers | Results must be valid and repeatable |