ELV

Fire Alarm Systems

A fire alarm system detects fire early, warns people and starts the building's fire safety actions. In the region designs usually follow NFPA 72 or BS 5839-1 with EN 54 listed devices, plus the local civil defence requirements.

Conventional or addressable

  • Conventional: devices are wired in zones. The panel knows which zone is in alarm, not which device. Suits small buildings.
  • Addressable: every device has an address on a loop, so the panel shows the exact location. Standard for most commercial projects.
  • Loops: wired as a loop (Class A / return path) with short-circuit isolators, so one cable fault does not lose the whole loop.
  • Cable: fire-resistant cable (standard or enhanced grade per BS 5839-1) fixed with metal clips, not plastic ties alone.

Main devices

  • Detectors: optical smoke, heat (fixed or rate-of-rise), multi-sensor, beam, aspirating (ASD) and flame.
  • Manual call points on escape routes and at exits.
  • Sounders, beacons and voice alarm to warn occupants. Visual alarms are needed where people are deaf or the area is noisy.
  • Interface modules to monitor sprinkler flow switches and to control fans, dampers, lifts and doors.

Cause & effect

  • A cause & effect matrix lists every input (detector zone, flow switch, call point) against every output (sounders, AHU shutdown, damper close, lift homing, door release, PA message).
  • Agree the matrix with the fire consultant and authority before programming the panel.
  • Witness every line of the matrix during commissioning and keep the signed copy in the O&M manual.

Typical point detector coverage (flat ceiling)

StandardSmoke detectorHeat detector
BS 5839-1Max 7.5 m from any pointMax 5.3 m from any point
NFPA 72Nominal 9.1 m (30 ft) spacingPer listed spacing of the detector
Good to knowKeep smoke detectors at least 1 m from supply air diffusers (BS 5839-1). Air flow can blow smoke away from the detector and delay the alarm.