Fiber Testing: OLTS, OTDR and More
Fiber testing proves that each link is installed correctly and that its loss is within the budget. TIA and ISO/IEC standards define two levels: Tier 1 (basic) and Tier 2 (extended).
The tests
- Visual fault locator (VFL): red light to check continuity and find breaks or tight bends near the ends.
- End-face inspection: a fiber microscope checks every connector against IEC 61300-3-35 before mating. Dirt is the first cause of failed links.
- Tier 1 – OLTS (light source and power meter): measures insertion loss of the whole link at two wavelengths (850/1300 nm multimode, 1310/1550 nm single-mode). This is the pass/fail test.
- Tier 2 – OTDR: sends pulses and plots a trace of every connector, splice and bend along the link with its distance and loss. Use it to prove workmanship and locate faults.
- Polarity and length are recorded with the Tier 1 results.
Doing it right
- Set the reference with the one-jumper method (TIA Method B) so the result includes both end connectors.
- For multimode, use an Encircled Flux compliant launch condition (IEC 61280-4-1) for repeatable results.
- With an OTDR, use launch and receive fibers so the first and last connectors are measured, and test from both ends to average splice loss.
- Compare each result with the calculated loss budget, not with a generic number. Use the fiber loss budget calculator in this site.
TIA-568 maximum loss values
| Component | Max loss |
|---|---|
| Mated connector pair | 0.75 dB |
| Fusion or mechanical splice | 0.3 dB |
| Multimode fiber | 3.5 dB/km at 850 nm · 1.5 dB/km at 1300 nm |
| Single-mode, inside plant | 1.0 dB/km |
| Single-mode, outside plant | 0.5 dB/km |